Pid processing algorithm
The drawing below is intended to be a representation of what
the computer thinks is the state of the servo actuator
at any point in time. The computer updates all the information
on a fixed interval and runs the PID computations.
As you can see, a lot of the information is based solely
on mechanical aspects of how the servo actuator was built,
and other measurements you can take on the physical system.
Other parts of the information is spec'ed out, like the dead band
tolerance. The rest of the information is ascertained prior to
the PID computation, like the angle and the set point.
Remember, the drawing represents a somewhat ideal example
, so a real world version may need to be adjusted to incorporate "as built"
values for some of the information.
The computational aspect of the PID routine generally
follows this algorithm (At least this is what I have come up with, based on my
research and experimentation... ), using the state information of the
servo actuator:
Determine the PID Gains. These are fixed once the system is
"tuned". More on tuning PID gains in a later episode...
Then, on a "timer basis" do the following steps:
1. If the angle is outside the soft stops, halt PID processing
because something is broken. Skip all the following steps
and don't drive the output arm. Don't allow PID processing the
next time around.
2. Retrieve the set point and angle of the output arm
3. Determine if the angle is outside the dead band
4. If not skip all the steps and don't drive the output arm at all, but
allow PID processing the next time around
5. If so, compute the error between the set point and angle
and remember the sign of the error
6. Compute the P term using the error and Pgain
7, Limit the Pterm to the max controller output - "offset". Recall that
the "offset" is the amount of "shove" to apply to get the output
arm to move at all...to overcome the fact it is sitting still.
8. Compute the difference between the last angle reading and the
current one. Doing this instead of using the difference in the error
from last time to this time avoids using the set point in this
computation and thus avoids the "derivative kick".
(I believe the Atmel app notes mentions this, but the set point in the
Microchip app notes is fixed... Google this to learn more)
9. Limit this to a physically possible range... ( remember the speed spec.. deg/sec)
10. Compute the Dterm using this and the Dgain ( remember the Dterm acts in the
opposite manner as the Pterm).
11. Limit the Dterm to the max controller output - "offset" (keep sign straight)
12. Avoid "integral windup" (there are several ways to do this)
(See the Atmel and Microchip app notes, and Google this to learn more)
13. If the Iterm is needed, add the error to the running total of error.
14. Compute the I term using the running error total and the Igain
15. Limit the Iterm to the max controller output - "offset"
16. Add the P, I, and D terms
17. Limit the sum of the P, I, and D terms to the max controller output - "offset"
18. Use the controller output and the "offset" to determine what to do to get the
servo actuator to move the desired direction and magnitude. This normally
translates to setting the duty cycle of a PWM waveform going to the
servo actuator coil and selecting the direction of the current through
it depending on the sign of the controller output)
19. Repeat all the steps starting at #1 after a fixed time
Like I said... a simple math problem
SteveH
shoutchen is offline Find More Posts by shoutchen